Dear All
I have CPU 317-2pn/dp and I want to use it as a getaway i.e (I read data from circuit breakers via profibus and send this data via modbus RTU to central control) and I use CP341 module.
Did this CPU support this purpose (can I use this cpu in these tow protocols)?
What can I write in this program (Program architecture)?
Best Regards
Siemens profibus and modbus
-
- Posts: 258
- Joined: Fri Apr 03, 2009 3:24 pm
- Location: Bosnia and Herzegovina
Re: Siemens profibus and modbus
CP341 is expensive, and need a even more expensive dongle for Modbus. Since your CPU has a PN port, better use S7-1211+CM1241RS485 for a gateway. At least 85% cheaper.
-
- Posts: 244
- Joined: Sat Oct 22, 2011 7:12 am
Re: Siemens profibus and modbus
thank you so much