I want to number connections in my project but i don’t want to number connections between phases, neutral and ground[interruption points](L1, L2, L3, N, PE). I wipe away unwanted connection numbers manually. It is a waste of time. How can I solve it?
EPLAN P8 1.7 connection numbering
-
- Posts: 186
- Joined: Sun Feb 12, 2006 5:47 pm
- Location: Europe
Re: EPLAN P8 1.7 connection numbering
Hi,
In terminal properties under Function definition should stay N-terminal or PE-terminal or SH-terminal or you can make your own function definition. In this case terminals are not numbered in automatic numbering.
regards
In terminal properties under Function definition should stay N-terminal or PE-terminal or SH-terminal or you can make your own function definition. In this case terminals are not numbered in automatic numbering.
regards