i installed pcs7 v8.1 on windows server 2008 data center when pcs7 was installing simatic net error happened (CP1623(1):AN INTERNAL ERROR OCCURRED ). after install finished i go to device manager and saw cp1623 with a yellow exclamation point and in the PC\pg interface i couldn't see cp1623
how could i fix it and why this error happened
problem with cp1623
-
- Posts: 24
- Joined: Thu Nov 08, 2007 6:46 pm
- Location: India
Re: problem with cp1623
Please complete installation of PCS7 without CP1623 installed. Install CP1623 after the installation is complete.. It will work.