Relay tuning result for Siemens FB58

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
kkzh
Posts: 8
Joined: Mon Sep 13, 2010 3:55 pm

Relay tuning result for Siemens FB58

Post by kkzh »

I have to adjust 10 PID loops and done some relay tuning exercises with my S7 program.

I had obtained the Ultimate Gains (Ku) and Ultimate Periods (Pu) of my PID's with relay tuning method.

I would like to know, what is the relationship between my relay tuning results and the Siemens PID parameters. I am using some FB58 and some FB41.

For example one of my relay tuning result for FB58 is:

Ku = 101.86%per deg C

Pu = 120 sec

According to Zeigler-Nichols rule of tuning constants, I get:

Gain = 61.12% per deg C(by 4d/a.pi), Ti = 60 sec (by Pu/2) , Td = 15 sec(by Pu/8)

What are the corresponding parameters for implementation in FB58, if the cycle time of PID is 0.4 sec:

Gain =?, TI =?, TD=?

In the FB58, there is a parameter D_F which is quite interesting in this case.

Thank you for your help in advance.