HELP!!!URGENT vijeo citect work only with ebool and not inte

Прочие SCADA: iFix, InTouch, Citect, ...
aacmpy
Posts: 6
Joined: Thu Jul 09, 2015 2:57 pm

HELP!!!URGENT vijeo citect work only with ebool and not inte

Post by aacmpy »

Hello
I created a program in unity pro and HMI local on Vijeo Citect and communication between them realize by OFS OPC FACTORY .
before the program and hmi works very well but two day past
vijeo citect recoveres only ebool variables and not integer variables .
could you please help me in this problem
aacmpy
Posts: 6
Joined: Thu Jul 09, 2015 2:57 pm

Re: HELP!!!URGENT vijeo citect work only with ebool and not

Post by aacmpy »

up
Schtiel
Site Admin
Posts: 1122
Joined: Wed Sep 06, 2006 12:03 pm
Location: CIS

Post by Schtiel »

Post screenshots of your problem. Did you try your project on another PC with fresh installation of Citect?
aacmpy
Posts: 6
Joined: Thu Jul 09, 2015 2:57 pm

Re: HELP!!!URGENT vijeo citect work only with ebool and not

Post by aacmpy »

BEFORE
Image
AFTER
Image
apilife
Posts: 56
Joined: Tue Jul 06, 2010 7:03 pm

Re: HELP!!!URGENT vijeo citect work only with ebool and not

Post by apilife »

Do you use located variables? Or do you use the data dictionary with OFS?
And did you change (rebuild) the Unity Pro program?
NikitaF
Posts: 7
Joined: Tue Apr 08, 2014 10:53 am

Re: HELP!!!URGENT vijeo citect work only with ebool and not

Post by NikitaF »

If you rebuild unity program, you need to update XVM/STA file in OFS config.