I created a program in unity pro and HMI local on Vijeo Citect and communication between them realize by OFS OPC FACTORY .
before the program and hmi works very well but two day past
vijeo citect recoveres only ebool variables and not integer variables .
could you please help me in this problem
HELP!!!URGENT vijeo citect work only with ebool and not inte
-
- Posts: 6
- Joined: Thu Jul 09, 2015 2:57 pm
-
- Posts: 6
- Joined: Thu Jul 09, 2015 2:57 pm
-
- Posts: 6
- Joined: Thu Jul 09, 2015 2:57 pm
-
- Posts: 56
- Joined: Tue Jul 06, 2010 7:03 pm
Re: HELP!!!URGENT vijeo citect work only with ebool and not
Do you use located variables? Or do you use the data dictionary with OFS?
And did you change (rebuild) the Unity Pro program?
And did you change (rebuild) the Unity Pro program?
-
- Posts: 7
- Joined: Tue Apr 08, 2014 10:53 am
Re: HELP!!!URGENT vijeo citect work only with ebool and not
If you rebuild unity program, you need to update XVM/STA file in OFS config.