I have found errors when I upload panel p41 ( PLC B&R )

другие контроллеры
letranlong
Posts: 85
Joined: Tue Jul 15, 2014 5:05 pm

I have found errors when I upload panel p41 ( PLC B&R )

Post by letranlong »

please help me.
when I upload panel p41, but me upload being errors.
i have a question for your help, I have found errors when I upload panel p41. those errors are shown that I send attach emage. could you help me how to fix those errors
https://goo.gl/Vj2dOS
https://goo.gl/EgsUSf
letranlong
Posts: 85
Joined: Tue Jul 15, 2014 5:05 pm

Re: I have found errors when I upload panel p41 ( PLC B&R )

Post by letranlong »

could you help me how to fix those errors
edomali
Posts: 1
Joined: Sat Jan 30, 2016 7:18 pm

Re: I have found errors when I upload panel p41 ( PLC B&R )

Post by edomali »

Automation studio help :
The object (task, module, variable) can't be identified on the controller. The reason could be an incorrect connection description (CD parameter) or an invalid object hierarchy (e.g. local variable registered on the CPU).
For PVI applications that access a controller with AR 3.00 or higher (SG4) and AR 2.30 (SGC) via the INA2000 line with a PVI version below V3.0.0, error 4813 is output for all global variables, and error 4806 is output for all local variables.