please help me.
when I upload panel p41, but me upload being errors.
i have a question for your help, I have found errors when I upload panel p41. those errors are shown that I send attach emage. could you help me how to fix those errors
https://goo.gl/Vj2dOS
https://goo.gl/EgsUSf
I have found errors when I upload panel p41 ( PLC B&R )
-
- Posts: 85
- Joined: Tue Jul 15, 2014 5:05 pm
-
- Posts: 85
- Joined: Tue Jul 15, 2014 5:05 pm
Re: I have found errors when I upload panel p41 ( PLC B&R )
could you help me how to fix those errors
-
- Posts: 1
- Joined: Sat Jan 30, 2016 7:18 pm
Re: I have found errors when I upload panel p41 ( PLC B&R )
Automation studio help :
The object (task, module, variable) can't be identified on the controller. The reason could be an incorrect connection description (CD parameter) or an invalid object hierarchy (e.g. local variable registered on the CPU).
For PVI applications that access a controller with AR 3.00 or higher (SG4) and AR 2.30 (SGC) via the INA2000 line with a PVI version below V3.0.0, error 4813 is output for all global variables, and error 4806 is output for all local variables.
The object (task, module, variable) can't be identified on the controller. The reason could be an incorrect connection description (CD parameter) or an invalid object hierarchy (e.g. local variable registered on the CPU).
For PVI applications that access a controller with AR 3.00 or higher (SG4) and AR 2.30 (SGC) via the INA2000 line with a PVI version below V3.0.0, error 4813 is output for all global variables, and error 4806 is output for all local variables.