Good day!
i try connect CPU315-2dp with CP341-1 (343-1-ex11-0xe0)
i can ping CP. When i opened hardware in simatic and open module information i can see that CPU in Run mode.
i can see CPU mode. But i dont view blocks on CPU.
Whats wrong?
Picture with diagnostic.
Image
dieego
Posts: 14
Joined: Wed Oct 06, 2010 1:17 pm

Re: connection CPU315-2dp with CP341-1

Post by dieego »

this is my hardware
Image
CoMod
Site Admin
Posts: 3992
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia

Re: connection CPU315-2dp with CP341-1

Post by CoMod »

Upload Station to PG IE
Image
omar_yousry
Posts: 2
Joined: Mon Feb 06, 2017 8:59 am

Re: connection CPU315-2dp with CP341-1

Post by omar_yousry »

First of all how are you connected to the PLC? (Ethernet, is there multi level switch? if yes you need to indicate the Ethernet switch you are connected to as the gateway).
Second you can try to connect manually if not visible in accessible nodes, you can put Rack and slot No. then add the IP address if the network uses TCP/IP, or the MAC address with ISO communication (Set PC/PG interface).
this way you can connect even if not present in accessible nodes.