[?+]: TIA Portal V13 Incompatible device SCALANCE W748-1

Post by webbber »

HI all..

I got the strrange problem... I am using a scalance -
SCALANCE W748-1 M12 which address is set to 172.10.0.65 (boom) *update same IP for PLC (boom)

behind it - using its build-in NAT there is a PLC.

What is strange - when i want to connect to it via cable - everything is fine.
when my friend connects it is ok.

But when i want to connect using my filed PG - i am all the time getting a message - incompatible device found at address...

What is strange i use to have this problem before - then small work around helped. Built-in Pg wi-fi was getting this error but USB tp-link wifi worked.

Right now I am getting this issue on both of them.

Any help? Any clues?

Please this plc is a part of moving machine and i really can not follow it with cable
Image
CoMod
Site Admin
Posts: 3992
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia

Re: [?]: TIA Portal V13 Incompatible device

Post by CoMod »

Install Update or Service Pack 1 for TIA Portal V13 https://support.industry.siemens.com/cs ... ia-portal)
The new ET 200SP CPUs are configured exclusively in the Totally Integrated Automation Portal with STEP 7 Professional V13 and higher.
The STEP7 V13 Update 3 is available for download under “Updates for STEP 7 V13 and WinCC V13“, entry ID:
https://support.industry.siemens.com/cs ... -wincc-v13
webbber
Posts: 4
Joined: Wed Feb 24, 2016 10:36 am

Re: [?]: TIA Portal V13 Incompatible device SCALANCE W748-1

Post by webbber »

It is not that - i got SP2

Image

and also tia updater - finds nothing to be updated..


EDIT: it is solved! What i was doing wrong is not puting in the gateway! When have put on my wifi settings the gateway same address as scalance it worked!

@Moderator - please close the topic.