1)CPU S7-315-2 PN/DP 315-2EH13-0AB0 - старая ревизия ЦПУ. Пришивку обновил до последней v.2.6.12
2)ET 200M PROFINET (IM153-4 HF)
3)AI 8*13 BIT 331-1KF01-0AB0 подключен к ЕТ.
ЕТ и ЦПУ пингуются.
После загрузки ПО в ЦПУ процессор вываливается в STOP. Только если в программе отсутствуют опросы входов AI, ЦПУ остается в RUN.
Есть ли какие-то нюансы настройки PROFINET, загрузки ПО или адрессации входов/выходов, подключенных к ЕТ? В чем проблема?
Order No./ Description Component Version
6ES7 315-2EH13-0AB0 Hardware 1
- - - Firmware V 2.6.12
Boot Loader Firmware expansion A 6.11.8
Rack: 0
Slot: 2
Serial number: S C-UDL863922006
Event 1 of 76: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 20
Module address: 12
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
03:48:36.520 PM 04/10/2018
(Coding: 16# 4563 FF84 8C70 0C23 0014 000C)
Event 2 of 76: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 256
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
03:48:36.517 PM 04/10/2018
(Coding: 16# 2942 FE7A 0020 0100 0000 0000)
Event 3 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
03:46:31.513 PM 04/10/2018
(Coding: 16# 4302 FF68 C700 0000 0B13 7713)
Event 4 of 76: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by stop switch being activated
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
03:46:31.509 PM 04/10/2018
(Coding: 16# 1381 FE64 C772 4303 0B13 7713)
Event 5 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by stop switch being activated
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
03:46:31.420 PM 04/10/2018
(Coding: 16# 4301 FF46 C772 4303 0813 7713)
Event 6 of 76: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
03:46:13.733 PM 04/10/2018
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 7 of 76: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
03:46:04.708 PM 04/10/2018
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 8 of 76: Event ID 16# 4303
STOP caused by stop switch being activated
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
03:46:02.083 PM 04/10/2018
(Coding: 16# 4303 FF84 0000 0000 0000 0000)
Event 9 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: RUN
External error, Incoming event
03:45:46.839 PM 04/10/2018
(Coding: 16# 596D 0008 C050 07FD 0000 0001)
Event 10 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
03:13:04.086 PM 04/10/2018
(Coding: 16# 4302 FF68 C700 0000 0B14 7714)
Event 11 of 76: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
03:13:04.083 PM 04/10/2018
(Coding: 16# 1381 FE64 C772 4304 0B14 7714)
Event 12 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
03:13:03.998 PM 04/10/2018
(Coding: 16# 4301 FF46 C772 4304 0B14 7714)
Event 13 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: STOP (internal)
External error, Incoming event
03:12:53.067 PM 04/10/2018
(Coding: 16# 596D 0004 C050 07FD 0000 0001)
Event 14 of 76: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
03:12:51.877 PM 04/10/2018
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 15 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
03:10:36.911 PM 04/10/2018
(Coding: 16# 4302 FF68 C700 0000 0B14 7714)
Event 16 of 76: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
03:10:36.908 PM 04/10/2018
(Coding: 16# 1381 FE64 C772 4563 0B14 7714)
Event 17 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
03:10:36.825 PM 04/10/2018
(Coding: 16# 4301 FF46 C772 4563 0B14 7714)
Event 18 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: STOP (internal)
External error, Incoming event
03:10:25.886 PM 04/10/2018
(Coding: 16# 596D 0004 C050 07FD 0000 0001)
Event 19 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: STOP (internal)
External error, Incoming event
02:38:25.140 PM 04/10/2018
(Coding: 16# 596D 0004 C050 07FD 0000 0001)
Event 20 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: STOP (internal)
External error, Incoming event
02:35:47.966 PM 04/10/2018
(Coding: 16# 596D 0004 C050 07FD 0000 0001)
Event 21 of 76: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 20
Module address: 12
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
02:27:45.243 PM 04/10/2018
(Coding: 16# 4563 FF84 8C70 0C23 0014 000C)
Event 22 of 76: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 256
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
02:27:45.240 PM 04/10/2018
(Coding: 16# 2942 FE7A 0020 0100 0000 0000)
Event 23 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
02:27:44.235 PM 04/10/2018
(Coding: 16# 4302 FF68 C700 0000 0B14 7714)
Event 24 of 76: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
02:27:44.232 PM 04/10/2018
(Coding: 16# 1381 FE64 C772 4563 0B14 7714)
Event 25 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:27:44.145 PM 04/10/2018
(Coding: 16# 4301 FF46 C772 4563 0B14 7714)
Event 26 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: STOP (internal)
External error, Incoming event
02:27:33.189 PM 04/10/2018
(Coding: 16# 596D 0004 C050 07FD 0000 0001)
Event 27 of 76: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 20
Module address: 12
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
02:25:50.699 PM 04/10/2018
(Coding: 16# 4563 FF84 8C70 0C23 0014 000C)
Event 28 of 76: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 256
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
02:25:50.696 PM 04/10/2018
(Coding: 16# 2942 FE7A 0020 0100 0000 0000)
Event 29 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
02:25:49.691 PM 04/10/2018
(Coding: 16# 4302 FF68 C700 0000 0B13 7713)
Event 30 of 76: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
02:25:49.688 PM 04/10/2018
(Coding: 16# 1381 FE64 C772 4563 0B13 7713)
Event 31 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:25:49.601 PM 04/10/2018
(Coding: 16# 4301 FF46 C772 4563 0813 7713)
Event 32 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: STOP (internal)
External error, Incoming event
02:25:38.654 PM 04/10/2018
(Coding: 16# 596D 0004 C050 07FD 0000 0001)
Event 33 of 76: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
02:25:31.910 PM 04/10/2018
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 34 of 76: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
02:25:21.894 PM 04/10/2018
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 35 of 76: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 20
Module address: 12
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
02:16:41.145 PM 04/10/2018
(Coding: 16# 4563 FF84 8C70 0C23 0014 000C)
Event 36 of 76: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 256
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
02:16:41.142 PM 04/10/2018
(Coding: 16# 2942 FE7A 0020 0100 0000 0000)
Event 37 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
02:12:50.138 PM 04/10/2018
(Coding: 16# 4302 FF68 C700 0000 0B14 7714)
Event 38 of 76: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
02:12:50.135 PM 04/10/2018
(Coding: 16# 1381 FE64 C772 4563 0B14 7714)
Event 39 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:12:50.048 PM 04/10/2018
(Coding: 16# 4301 FF46 C772 4563 0B14 7714)
Event 40 of 76: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 20
Module address: 12
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
02:11:47.503 PM 04/10/2018
(Coding: 16# 4563 FF84 8C70 0C23 0014 000C)
Event 41 of 76: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 256
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
02:11:47.500 PM 04/10/2018
(Coding: 16# 2942 FE7A 0020 0100 0000 0000)
Event 42 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
02:11:46.496 PM 04/10/2018
(Coding: 16# 4302 FF68 C700 0000 0B14 7714)
Event 43 of 76: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
02:11:46.493 PM 04/10/2018
(Coding: 16# 1381 FE64 C772 4563 0B14 7714)
Event 44 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:11:46.403 PM 04/10/2018
(Coding: 16# 4301 FF46 C772 4563 0B14 7714)
Event 45 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: STOP (internal)
External error, Incoming event
02:11:35.479 PM 04/10/2018
(Coding: 16# 596D 0004 C050 07FD 0000 0001)
Event 46 of 76: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 20
Module address: 12
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
02:10:06.167 PM 04/10/2018
(Coding: 16# 4563 FF84 8C70 0C23 0014 000C)
Event 47 of 76: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 256
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
02:10:06.164 PM 04/10/2018
(Coding: 16# 2942 FE7A 0020 0100 0000 0000)
Event 48 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
02:10:05.159 PM 04/10/2018
(Coding: 16# 4302 FF68 C700 0000 0B14 7714)
Event 49 of 76: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
02:10:05.156 PM 04/10/2018
(Coding: 16# 1381 FE64 C772 4563 0B14 7714)
Event 50 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:09:54.067 PM 04/10/2018
(Coding: 16# 4301 FF46 C772 4563 0B14 7714)
Event 51 of 76: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 20
Module address: 12
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
12:11:34.027 AM 01/01/1994
(Coding: 16# 4563 FF84 8C70 0C23 0014 000C)
Event 52 of 76: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 256
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
12:11:34.024 AM 01/01/1994
(Coding: 16# 2942 FE7A 0020 0100 0000 0000)
Event 53 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
12:11:33.020 AM 01/01/1994
(Coding: 16# 4302 FF68 C700 0000 0B14 7714)
Event 54 of 76: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
12:11:33.016 AM 01/01/1994
(Coding: 16# 1381 FE64 C772 4563 0B14 7714)
Event 55 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
12:11:21.923 AM 01/01/1994
(Coding: 16# 4301 FF46 C772 4563 0B14 7714)
Event 56 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: STOP (internal)
External error, Incoming event
12:11:10.975 AM 01/01/1994
(Coding: 16# 596D 0004 C050 07FD 0000 0001)
Event 57 of 76: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic interrupt OB (OB 35)
Priority class: 12
FC number: 20
Module address: 12
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
12:10:06.707 AM 01/01/1994
(Coding: 16# 4563 FF84 8C70 0C23 0014 000C)
Event 58 of 76: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 256
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
12:10:06.704 AM 01/01/1994
(Coding: 16# 2942 FE7A 0020 0100 0000 0000)
Event 59 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
12:10:05.700 AM 01/01/1994
(Coding: 16# 4302 FF68 C700 0000 0B13 7713)
Event 60 of 76: Event ID 16# 1381
Request for manual warm restart
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
12:10:05.696 AM 01/01/1994
(Coding: 16# 1381 FE64 C772 0000 0B13 7713)
Event 61 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
12:10:05.608 AM 01/01/1994
(Coding: 16# 4301 FF46 C772 0000 0813 7713)
Event 62 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: STOP (internal)
External error, Incoming event
12:09:38.596 AM 01/01/1994
(Coding: 16# 596D 0004 C050 07FD 0000 0001)
Event 63 of 76: Event ID 16# 596D
The existing network configuration do not correspond to the system requirements or configuration
logical address of the error-detecting module 2045
cause of error: Bps not suitable for PROFINET IO
operating mode: STOP (internal)
External error, Incoming event
12:08:29.010 AM 01/01/1994
(Coding: 16# 596D 0004 C050 07FD 0000 0001)
Event 64 of 76: Event ID 16# 430E
Memory reset executed
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
Incoming event
12:03:12.475 AM 01/01/1994
(Coding: 16# 430E FF23 0000 0000 0000 0000)
Event 65 of 76: Event ID 16# 4546
STOP caused by CPU memory management
Previous operating mode: STOP (own initialization)
Requested operating mode: STOP (memory reset)
Internal error, Incoming event
12:03:10.969 AM 01/01/1994
(Coding: 16# 4546 FF32 C0C0 8FFE 0000 0000)
Event 66 of 76: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
12:03:10.969 AM 01/01/1994
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 67 of 76: Event ID 16# 6522
Illegal module: replace module and reset memory
Operating mode: STOP (own initialization)
Internal error, Incoming event
12:03:10.969 AM 01/01/1994
(Coding: 16# 6522 FF03 0000 0001 0001 8FFE)
Event 68 of 76: Event ID 16# 4580
STOP: backup buffer contents inconsistent (no transition to RUN)
Previous operating mode: No voltage
Requested operating mode: STOP (internal)
Internal error, Incoming event
12:02:57.077 AM 01/01/1994
(Coding: 16# 4580 FFF4 0000 0002 0000 0000)
Event 69 of 76: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
12:02:57.076 AM 01/01/1994
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 70 of 76: Event ID 16# 4303
STOP caused by stop switch being activated
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
12:02:52.939 AM 01/01/1994
(Coding: 16# 4303 FF84 0000 0000 0000 0000)
Event 71 of 76: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last non backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
12:02:18.956 AM 01/01/1994
(Coding: 16# 4302 FF68 C700 0000 0013 7713)
Event 72 of 76: Event ID 16# 1381
Request for manual warm restart
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last non backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the in the current operating mode
Incoming event
12:02:18.952 AM 01/01/1994
(Coding: 16# 1381 FE64 C772 0000 0013 7713)
Event 73 of 76: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last non backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
12:02:18.704 AM 01/01/1994
(Coding: 16# 4301 FF46 C772 0000 0013 7713)
Event 74 of 76: Event ID 16# 430E
Memory reset executed
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
Incoming event
12:00:03.336 AM 01/01/1994
(Coding: 16# 430E FF23 0000 0000 0000 0000)
Event 75 of 76: Event ID 16# 4546
STOP caused by CPU memory management
Previous operating mode: STOP (own initialization)
Requested operating mode: STOP (memory reset)
Internal error, Incoming event
12:00:00.424 AM 01/01/1994
(Coding: 16# 4546 FF32 C0C0 0104 0000 0000)
Event 76 of 76: Event ID 16# 4580
STOP: backup buffer contents inconsistent (no transition to RUN)
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Internal error, Incoming event
12:00:00.000 AM 01/01/1994
(Coding: 16# 4580 FFF3 0000 0000 0000 0000)