Hi, if some one made Modicon M241 connection with weintek MT8102 iE?
I did what manual of Weintek sey.
Is there special setings in Somachine progect of M241?
Thanks
Modicon M241 connection with weintek MT8102 iE
-
- Posts: 26
- Joined: Tue Jun 17, 2008 10:48 am
- Location: Europe
-
- Posts: 26
- Joined: Tue Jun 17, 2008 10:48 am
- Location: Europe
Re: Modicon M241 connection with weintek MT8102 iE
The problem is solved.
Just chenge of IP addres end subnet mask
Old one was PLC IP :10.10.9.100 SM: 255.0.0.0
HMI IP: 10.10.9.101 SM: 255.0.0.0
New on PLC IP: 192.168.5.10 SM: 255.255.255.0
HMI IP: 192.168.5.11 SM: 255.255.255.0
End connection is ok now.
Just chenge of IP addres end subnet mask
Old one was PLC IP :10.10.9.100 SM: 255.0.0.0
HMI IP: 10.10.9.101 SM: 255.0.0.0
New on PLC IP: 192.168.5.10 SM: 255.255.255.0
HMI IP: 192.168.5.11 SM: 255.255.255.0
End connection is ok now.