How to configuration for Momentum Communication 170 PNT 110

другие контроллеры
danhtran
Posts: 3
Joined: Fri Sep 23, 2016 6:44 am

How to configuration for Momentum Communication 170 PNT 110

Post by danhtran »

Dear Experts,

I'm a newbie for Momentum PLC. Please support me with the below situation:

I'm trying to program a Modicon Momentum PLC, the entire system of the momentum as below:
1. Station 1:
- Modicon Momentum Processor 171 CCC 760 10
- Communication Adapter Momentum 171 INT 110 00
- I/O base: Momentum 32 channel Digital Input Module 170 ADI 350 00

2. Station 2:
- Communication module for Momentum I/O 170 PNT 110 20
- I/O Base: Digital 16 In/16 Out Module 170 ADM 350 10

I can use Concept V2.6 SR7 to config and program for station 1 well.
But I don't know how to config and send data address for station 2 which will connect to station 1 via Modbus plus.
Please advise me for this case!

Much appreciate for your kindly support!

Regards,
Danh
SE_support
Posts: 101
Joined: Thu Aug 29, 2013 4:11 pm

Re: How to configuration for Momentum Communication 170 PNT

Post by SE_support »

Hi Danhtran,

well, the 171CCC76010 is the PLC and 171ADI35000 is the IO - put both together and the base 1 is ready.

For base 2 take 171INT1100 and 170ADM35000 - put both together and connect to base 1 via IO-Bus (Interbus) cable.

The communication adapter 170PNT for modbus+ can't be installed on base 1. To connect both bases via Modbus+ you will need additional modbus+ adapter for PLC.
danhtran
Posts: 3
Joined: Fri Sep 23, 2016 6:44 am

Re: How to configuration for Momentum Communication 170 PNT

Post by danhtran »

SE_support wrote:Hi Danhtran,

well, the 171CCC76010 is the PLC and 171ADI35000 is the IO - put both together and the base 1 is ready.

For base 2 take 171INT1100 and 170ADM35000 - put both together and connect to base 1 via IO-Bus (Interbus) cable.

The communication adapter 170PNT for modbus+ can't be installed on base 1. To connect both bases via Modbus+ you will need additional modbus+ adapter for PLC.
Hi SE_support,

Thanks for your support!
Sorry for my typo.
I mean that in Base 1, i put 171CCC76010 (PLC), 172 PNN 210 22 (Optional adapter for MBP) and 171ADI35000 together.
Then they connect to another IO base with Interbus card 171INT1100. I can finish it in Concept.

My issue here is i would like to connect another IO base via communication adapter 170PNT to that PLC.
But I can't find where I can config that card in Concept.
I've checked in "170 PNT Series Modbus Plus Communication Adapters for Momentum User Guide 870 USE 103 00 Version 2.0" manual however I don't understand clearly the way to do it.
Do we need to config that card in Concept or we only need to set address on that card and config in Concept/ Peer cop/ Specific Input/Output?
How can we know the source ref. of IO base in Specific Input/ output to set up properly?

Regards,
Danh
SE_support
Posts: 101
Joined: Thu Aug 29, 2013 4:11 pm

Re: How to configuration for Momentum Communication 170 PNT

Post by SE_support »

The connection via Modbus+ is not so easy to realize as Interbus, you need to know what is peer-cop communication.
You configure the base 1 in concept, the base 2 will be not configured in concept at all - I mean you don't see the 170PNT and 170ADM in Concept.
Both bases are connected or communicate via peer-cop.


Select Project → PLC configuration.
Select the Config. Extensions → Select Extensions list.
Check the Peer Cop box.
Select Config. Extensions → Peer Cop.

And now just read the concept manual how to configure the peer-cop.
danhtran
Posts: 3
Joined: Fri Sep 23, 2016 6:44 am

Re: How to configuration for Momentum Communication 170 PNT

Post by danhtran »

SE_support wrote:The connection via Modbus+ is not so easy to realize as Interbus, you need to know what is peer-cop communication.
You configure the base 1 in concept, the base 2 will be not configured in concept at all - I mean you don't see the 170PNT and 170ADM in Concept.
Both bases are connected or communicate via peer-cop.


Select Project → PLC configuration.
Select the Config. Extensions → Select Extensions list.
Check the Peer Cop box.
Select Config. Extensions → Peer Cop.

And now just read the concept manual how to configure the peer-cop.
Thank you @Se_Support!
(tyou)