Dear All,
Anybody can help on MODBUS TCP IP IN CONTROLLOGIX?
I have to read 30 Slaves data. And i am having 1756-L72 controller and 1756-EN2TR.
I have checked the sample code, which is downloaded from Rockwell Sample codes But with that I can read only 4 slaves Data only.
Sample Code: https://www.rockwellautomation.com/sear ... king=false
Thank You.
MODBUS TCP IP IN CONTROLLOGIX
-
- Posts: 2
- Joined: Tue Aug 27, 2019 4:29 pm
Re: MODBUS TCP IP IN CONTROLLOGIX
Hi
If you download the sample code, there are 2 manuals on the zip where you can read that the code only accept a maximum of 4 connections to unique IP address.
However, the manual also says that you can change this limitation modifyng the application (possibly on the tags).
Good luck!
If you download the sample code, there are 2 manuals on the zip where you can read that the code only accept a maximum of 4 connections to unique IP address.
However, the manual also says that you can change this limitation modifyng the application (possibly on the tags).
Good luck!