Comisioning PID Compact as multi-instance

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
Garrido95
Posts: 2
Joined: Sat Jul 25, 2020 11:08 am

Comisioning PID Compact as multi-instance

Post by Garrido95 »

Hi,

I want to use multi-instance PID, I have create some static pid_compact data tipe in a FB and i called this FB from OB30. ¿Is this a correct way to implement multi-instance PID in Tia Portal?
I use the instance db of the PIDs to configure it but I dont kwno how I can Start the PID. I want something similar like start button when use pid without multi-instance and appear in Commissioning of technology objects.

Thanks and sorry for my english (oo)
Answers to FAQs
Faq & Info
Faq & Info
Posts: 178
Joined: Thu Oct 13, 2005 6:42 pm
Location: Frequently Asked Questions – Часто Задаваемые Вопросы

Re: Comisioning PID Compact as multi-instance

Post by Answers to FAQs »

manual wrote:Call

PID_Compact is called in the constant time scale of a cycle interrupt OB.

If you call PID_Compact as a multi-instance DB, no technology object is created. No parameter assignment interface or commissioning interface is available. You must assign parameters for PID_Compact directly in the multi-instance DB and comision it via a watch table