Hello, I have a S7 315 2PN / DP (6es7 315-2EH14-0AB0) and now I am using Profibus CP 343-5 (6gk7343-5FA00-0XE0) No Problem Picture 1
However, I want to use CP 343-5 (6gk7 343-5FA01-0XE0) with S7 315 2PN / DP (6es7 315-2EH14-0AB0). Picture 2
I'm just creating the new project.
I installed the hardware according to the required product codes, but all the lights on 343-5 started flashing.
I have product 6es7 343-5FA01), I'm sure I chose the correct product codes. What am I missing?
CP 343-5 (343-5FA00-0XE0) module
System data files (SDB 1001 - 1002)
I installed it on the module CP 343-5 (343-5FA01-0XE0).
That's why he must be doing it. How can I fix?
Currently there is no connection between the CPU and the module. I cannot install software.
Can I hard reset the module?
Thank you for your help.
[?]: CP 343-5 Fault when replace new CP
-
- Site Admin
- Posts: 3992
- Joined: Thu Feb 16, 2006 3:25 pm
- Location: Russia
Re: [?]: CP 343-5 Fault when replace new CP
see Diagnostic buffer
for Profinet wrote:possible need to write Profinet Name for new CP
https://support.industry.siemens.com/cs ... t/19549525Unlike Profibus, in Profinet devices, in addition to the address, you must assign a network NAME to the device ... otherwise the device will be underconfigured and will be invisible in Profinet, although it will ping via IP.Before a PROFINET IO controller can address a PROFINET IO device a name has to be assigned to the PROFINET IO device.
This procedure has been chosen for PROFINET because names are easier to handle than complex IP addresses.
Assigning a device name for a concrete PROFINET IO device is like setting the PROFIBUS address for a DP slave.
===========
В отличии от Профибуса в Профинет устройствах надо помимо адреса необходимо назначать сетевое ИМЯ устройству... иначе устройство будет недоконфигурировано и будет невидимо в Профинете, хотя будет пинговаться по IP.
-
- Posts: 8
- Joined: Tue Nov 12, 2019 9:12 am
-
- Site Admin
- Posts: 3992
- Joined: Thu Feb 16, 2006 3:25 pm
- Location: Russia
-
- Posts: 8
- Joined: Tue Nov 12, 2019 9:12 am
-
- Site Admin
- Posts: 3992
- Joined: Thu Feb 16, 2006 3:25 pm
- Location: Russia
Re: [?]: CP 343-5 Fault when replace new CP
your CP is very old ... 20 year old version wit intel 386
new CP made with new hardware http://s7detali.narod.ru/NET/CP342.html
For testing: CPU + CP (not any other input/output module in Rack)
MRES for CPU for reset memory
load new config and see
P.S.
it is install automatically
new CP made with new hardware http://s7detali.narod.ru/NET/CP342.html
For testing: CPU + CP (not any other input/output module in Rack)
MRES for CPU for reset memory
load new config and see
P.S.
you are do not need install any SDB!I think I accidentally installed SDB 1001 and 1002 system files. and this is the result
it is install automatically
-
- Posts: 8
- Joined: Tue Nov 12, 2019 9:12 am
Re: [?]: CP 343-5 Fault when replace new CP
yes cp is too old.
but the same cpu also works the same model cp. MMres was made. The same project was uploaded again, the fault continues. Have you checked the log records?
Diagnostic buffer of module CPU 315-2 PN/DP
but the problem happened when I installed them? do you want to connect to the computer?
but the same cpu also works the same model cp. MMres was made. The same project was uploaded again, the fault continues. Have you checked the log records?
Diagnostic buffer of module CPU 315-2 PN/DP
Spoiler
Show
Order No./ Description Component Version
6ES7 315-2EH14-0AB0 Hardware 8
- - - Firmware V 3.2.16
Boot Loader Firmware expansion A 37.12.12
Rack: 0
Slot: 2
Serial number: S C-L7E587252019
Event 1 of 117: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 1002
No relevance for user (Z2): 0000 (Z3): 0000
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
08:41:41.505 PM 11/22/2020
(Coding: 16# 49A0 FF64 C17B 03EA 0000 0000)
Event 2 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP due to I/O management
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:41:41.439 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 4548 0B13 7713)
Event 3 of 117: Event ID 16# 6547
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number: 1002
DP master affected in rack 0 and slot 4
Station number: 0, slot number: 10
Operating mode: STOP (internal)
Internal error, Incoming event
08:41:41.413 PM 11/22/2020
(Coding: 16# 6547 FF04 C47B 03EA 0400 000A)
Event 4 of 117: Event ID 16# 6547
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number: 1001
DP master affected in rack 0 and slot 4
Station number: 0, slot number: 10
Operating mode: STOP (internal)
Internal error, Incoming event
08:41:20.264 PM 11/22/2020
(Coding: 16# 6547 FF04 C47B 03E9 0400 000A)
Event 5 of 117: Event ID 16# 4358
All modules are ready for operation
Operating mode: STOP (internal)
Incoming event
08:40:58.907 PM 11/22/2020
(Coding: 16# 4358 FF44 0000 0000 0000 0000)
Event 6 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:40:57.413 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 7 of 117: Event ID 16# 4548
STOP due to I/O management
Previous mode: RUN
Requested mode: STOP (internal)
Internal error, Incoming event
08:40:57.196 PM 11/22/2020
(Coding: 16# 4548 FF84 C000 0000 8005 0000)
Event 8 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:40:44.317 PM 11/22/2020
(Coding: 16# 4302 FF68 C700 0000 0B14 7714)
Event 9 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:40:44.316 PM 11/22/2020
(Coding: 16# 1381 1B64 C772 4304 0B14 7714)
Event 10 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 256 of the module with parameter assignment errors
Error type: configurable slot empty
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:40:44.289 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 8B08)
Event 11 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Input address: 256 of the module with parameter assignment errors
Error type: configurable slot empty
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:40:44.289 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 0B08)
Event 12 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:40:44.225 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 13 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:40:42.150 PM 11/22/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 14 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:39:38.739 PM 11/22/2020
(Coding: 16# 4302 FF68 C700 0000 0810 7710)
Event 15 of 117: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:39:38.738 PM 11/22/2020
(Coding: 16# 1382 1B64 C772 494E 0810 7710)
Event 16 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:39:38.646 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 494E 0810 7710)
Event 17 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:39:34.265 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 18 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:39:16.220 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 19 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:38:53.755 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 20 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:38:52.694 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 21 of 117: Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
08:38:33.689 PM 11/22/2020
(Coding: 16# 494E FF8F C000 0000 0000 0000)
Event 22 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:38:11.190 PM 11/22/2020
(Coding: 16# 4302 FF68 C700 0000 0813 7713)
Event 23 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by stop switch being activated
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:38:11.189 PM 11/22/2020
(Coding: 16# 1381 1B64 C772 4303 0813 7713)
Event 24 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by stop switch being activated
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:38:11.097 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 4303 0813 7713)
Event 25 of 117: Event ID 16# 4303
STOP caused by stop switch being activated
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:38:08.148 PM 11/22/2020
(Coding: 16# 4303 FF84 0000 0000 0000 0000)
Event 26 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:37:15.972 PM 11/22/2020
(Coding: 16# 4302 FF68 C700 0000 0810 7710)
Event 27 of 117: Event ID 16# 1382
Request for automatic warm restart
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:37:15.971 PM 11/22/2020
(Coding: 16# 1382 1B64 C772 0000 0810 7710)
Event 28 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:37:15.879 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 0000 0810 7710)
Event 29 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:37:11.537 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 30 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:36:53.451 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 31 of 117: Event ID 16# 4358
All modules are ready for operation
Operating mode: STOP (internal)
Incoming event
08:35:08.774 PM 11/22/2020
(Coding: 16# 4358 FF44 0000 0000 0000 0000)
Event 32 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:35:03.023 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 33 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:35:01.966 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 34 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:34:32.941 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 35 of 117: Event ID 16# 4358
All modules are ready for operation
Operating mode: STOP (internal)
Incoming event
08:34:30.244 PM 11/22/2020
(Coding: 16# 4358 FF44 0000 0000 0000 0000)
Event 36 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:34:24.706 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 37 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:34:23.649 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 38 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:34:07.628 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 39 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:33:50.990 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 40 of 117: Event ID 16# 430E
Memory reset executed
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
Incoming event
08:33:47.756 PM 11/22/2020
(Coding: 16# 430E FF23 0000 0000 0000 0000)
Event 41 of 117: Event ID 16# 4308
Memory reset started by switch setting
Previous operating mode: STOP (internal)
Requested operating mode: STOP (memory reset)
Incoming event
08:33:45.225 PM 11/22/2020
(Coding: 16# 4308 FF42 0000 0000 0000 0000)
Event 42 of 117: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 5
No relevance for user (Z2): 0000 (Z3): 000f
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
08:32:20.484 PM 11/22/2020
(Coding: 16# 49A0 FF64 C17B 0005 0000 000F)
Event 43 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:32:20.479 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 8B07)
Event 44 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Input address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:32:20.479 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 0B07)
Event 45 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:32:20.418 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 0000 0814 1714)
Event 46 of 117: Event ID 16# 5962
Parameter assignment error preventing startup in party-line parameters/communication bus parameters
Error type: I/O not ready, i.e. a module has not entered a type ID within the module monitoring time
Operating mode: STOP (internal)
External error, Incoming event
08:32:19.767 PM 11/22/2020
(Coding: 16# 5962 FF04 C17B 0005 0000 000F)
Event 47 of 117: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 5
No relevance for user (Z2): 0000 (Z3): 000f
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
08:31:57.551 PM 11/22/2020
(Coding: 16# 49A0 FF64 C17B 0005 0000 000F)
Event 48 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:31:57.545 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 8B07)
Event 49 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Input address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:31:57.545 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 0B07)
Event 50 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:31:57.482 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 0000 0814 1714)
Event 51 of 117: Event ID 16# 5962
Parameter assignment error preventing startup in party-line parameters/communication bus parameters
Error type: I/O not ready, i.e. a module has not entered a type ID within the module monitoring time
Operating mode: STOP (internal)
External error, Incoming event
08:31:55.501 PM 11/22/2020
(Coding: 16# 5962 FF04 C17B 0005 0000 000F)
Event 52 of 117: Event ID 16# 5962
Parameter assignment error preventing startup in party-line parameters/communication bus parameters
Error type: I/O not ready, i.e. a module has not entered a type ID within the module monitoring time
Operating mode: STOP (internal)
External error, Incoming event
08:31:07.341 PM 11/22/2020
(Coding: 16# 5962 FF04 C17B 0005 0000 000F)
Event 53 of 117: Event ID 16# 5962
Parameter assignment error preventing startup in party-line parameters/communication bus parameters
Error type: I/O not ready, i.e. a module has not entered a type ID within the module monitoring time
Operating mode: STOP (internal)
External error, Incoming event
08:28:20.274 PM 11/22/2020
(Coding: 16# 5962 FF04 C17B 0005 0000 000F)
Event 54 of 117: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 5
No relevance for user (Z2): 0000 (Z3): 000f
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
08:24:37.908 PM 11/22/2020
(Coding: 16# 49A0 FF64 C17B 0005 0000 000F)
Event 55 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 0 of the module with parameter assignment errors
Error type: configurable slot empty
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:24:37.902 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0000 8B08)
Event 56 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Input address: 0 of the module with parameter assignment errors
Error type: configurable slot empty
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:24:37.902 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0000 0B08)
Event 57 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:24:37.902 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 8B07)
Event 58 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Input address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:24:37.902 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 0B07)
Event 59 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:24:37.839 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 0000 0813 7713)
Event 60 of 117: Event ID 16# 5962
Parameter assignment error preventing startup in party-line parameters/communication bus parameters
Error type: I/O not ready, i.e. a module has not entered a type ID within the module monitoring time
Operating mode: STOP (internal)
External error, Incoming event
08:15:53.112 PM 11/22/2020
(Coding: 16# 5962 FF04 C17B 0005 0000 000F)
Event 61 of 117: Event ID 16# 4959
One or more modules not ready for operation
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
External error, Incoming event
08:15:52.530 PM 11/22/2020
(Coding: 16# 4959 FF44 C000 0000 0000 0000)
Event 62 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:14:47.517 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 63 of 117: Event ID 16# 430E
Memory reset executed
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
Incoming event
08:14:44.283 PM 11/22/2020
(Coding: 16# 430E FF23 0000 0000 0000 0000)
Event 64 of 117: Event ID 16# 6326
Memory reset request due to memory replacement
Operating mode: STOP (memory reset)
Incoming event
08:14:42.376 PM 11/22/2020
(Coding: 16# 6326 FF02 C450 8001 0000 1B79)
Event 65 of 117: Event ID 16# 4546
STOP caused by CPU memory management
Previous operating mode: STOP (own initialization)
Requested operating mode: STOP (memory reset)
Internal error, Incoming event
08:14:40.609 PM 11/22/2020
(Coding: 16# 4546 FF32 C0C0 0102 0000 0000)
Event 66 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:14:40.609 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 67 of 117: Event ID 16# 6526
Memory reset request due to memory replacement
Operating mode: STOP (own initialization)
Internal error, Incoming event
08:14:40.608 PM 11/22/2020
(Coding: 16# 6526 FF03 0000 0000 0001 0102)
Event 68 of 117: Event ID 16# 6326
Memory reset request due to memory replacement
Operating mode: STOP (own initialization)
Incoming event
08:14:40.608 PM 11/22/2020
(Coding: 16# 6326 FF03 C450 8001 0000 1B79)
Event 69 of 117: Event ID 16# 4580
STOP: backup buffer contents inconsistent (no transition to RUN)
Previous operating mode: No voltage
Requested operating mode: STOP (internal)
Internal error, Incoming event
08:14:14.476 PM 11/22/2020
(Coding: 16# 4580 FFF4 0000 0002 0000 0000)
Event 70 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:14:14.473 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 71 of 117: Event ID 16# 430E
Memory reset executed
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
Incoming event
08:14:05.339 PM 11/22/2020
(Coding: 16# 430E FF23 0000 0000 0000 0000)
Event 72 of 117: Event ID 16# 6326
Memory reset request due to memory replacement
Operating mode: STOP (memory reset)
Incoming event
08:14:05.284 PM 11/22/2020
(Coding: 16# 6326 FF02 C450 8001 1B79 0000)
Event 73 of 117: Event ID 16# 4546
STOP caused by CPU memory management
Previous operating mode: STOP (own initialization)
Requested operating mode: STOP (memory reset)
Internal error, Incoming event
08:14:00.629 PM 11/22/2020
(Coding: 16# 4546 FF32 C0C0 8FFE 0000 0000)
Event 74 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:14:00.629 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 75 of 117: Event ID 16# 6522
Illegal module: replace module and reset memory
Operating mode: STOP (own initialization)
Internal error, Incoming event
08:14:00.629 PM 11/22/2020
(Coding: 16# 6522 FF03 0000 0001 0001 8FFE)
Event 76 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:13:39.686 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 77 of 117: Event ID 16# 4358
All modules are ready for operation
Operating mode: STOP (internal)
Incoming event
08:13:13.513 PM 11/22/2020
(Coding: 16# 4358 FF44 0000 0000 0000 0000)
Event 78 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:13:09.040 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 79 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:13:07.984 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 80 of 117: Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
08:37:18.943 AM 10/26/2020
(Coding: 16# 494E FF8F C000 0000 0000 0000)
Event 81 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:36:25.050 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 82 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:36:25.049 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 83 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:36:24.960 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 84 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:36:03.140 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 85 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:35:00.130 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 86 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:35:00.129 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 87 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:35:00.040 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 88 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:34:39.548 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 89 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:33:42.681 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 90 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:33:42.679 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 91 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:33:42.591 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 92 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:33:40.660 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 93 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:31:42.079 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 94 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:31:42.078 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 95 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:31:41.991 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 96 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:31:39.971 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 97 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:29:59.121 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 98 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:29:59.120 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 99 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:29:59.031 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 100 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:29:57.057 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 101 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:25:08.204 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 102 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:25:08.203 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 103 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:25:08.114 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 104 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:25:05.325 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 105 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:06:22.793 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 106 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:06:22.792 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 107 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:06:22.704 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 108 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:05:56.580 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 109 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:04:41.840 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0810 7710)
Event 110 of 117: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:04:41.839 AM 10/26/2020
(Coding: 16# 1382 1B64 C772 494E 0810 7710)
Event 111 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:04:41.750 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 494E 0810 7710)
Event 112 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:04:37.298 AM 10/26/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 113 of 117: Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
04:22:52.342 PM 10/23/2020
(Coding: 16# 494E FF8F C000 0000 0000 0000)
Event 114 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
07:56:14.040 AM 10/23/2020
(Coding: 16# 4302 FF68 C700 0000 0810 7710)
Event 115 of 117: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
07:56:14.038 AM 10/23/2020
(Coding: 16# 1382 1B64 C772 494E 0810 7710)
Event 116 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
07:56:13.950 AM 10/23/2020
(Coding: 16# 4301 FF46 C772 494E 0810 7710)
Event 117 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
07:56:09.497 AM 10/23/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
6ES7 315-2EH14-0AB0 Hardware 8
- - - Firmware V 3.2.16
Boot Loader Firmware expansion A 37.12.12
Rack: 0
Slot: 2
Serial number: S C-L7E587252019
Event 1 of 117: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 1002
No relevance for user (Z2): 0000 (Z3): 0000
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
08:41:41.505 PM 11/22/2020
(Coding: 16# 49A0 FF64 C17B 03EA 0000 0000)
Event 2 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP due to I/O management
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:41:41.439 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 4548 0B13 7713)
Event 3 of 117: Event ID 16# 6547
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number: 1002
DP master affected in rack 0 and slot 4
Station number: 0, slot number: 10
Operating mode: STOP (internal)
Internal error, Incoming event
08:41:41.413 PM 11/22/2020
(Coding: 16# 6547 FF04 C47B 03EA 0400 000A)
Event 4 of 117: Event ID 16# 6547
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number: 1001
DP master affected in rack 0 and slot 4
Station number: 0, slot number: 10
Operating mode: STOP (internal)
Internal error, Incoming event
08:41:20.264 PM 11/22/2020
(Coding: 16# 6547 FF04 C47B 03E9 0400 000A)
Event 5 of 117: Event ID 16# 4358
All modules are ready for operation
Operating mode: STOP (internal)
Incoming event
08:40:58.907 PM 11/22/2020
(Coding: 16# 4358 FF44 0000 0000 0000 0000)
Event 6 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:40:57.413 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 7 of 117: Event ID 16# 4548
STOP due to I/O management
Previous mode: RUN
Requested mode: STOP (internal)
Internal error, Incoming event
08:40:57.196 PM 11/22/2020
(Coding: 16# 4548 FF84 C000 0000 8005 0000)
Event 8 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:40:44.317 PM 11/22/2020
(Coding: 16# 4302 FF68 C700 0000 0B14 7714)
Event 9 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:40:44.316 PM 11/22/2020
(Coding: 16# 1381 1B64 C772 4304 0B14 7714)
Event 10 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 256 of the module with parameter assignment errors
Error type: configurable slot empty
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:40:44.289 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 8B08)
Event 11 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Input address: 256 of the module with parameter assignment errors
Error type: configurable slot empty
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:40:44.289 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 0B08)
Event 12 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:40:44.225 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 13 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:40:42.150 PM 11/22/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 14 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:39:38.739 PM 11/22/2020
(Coding: 16# 4302 FF68 C700 0000 0810 7710)
Event 15 of 117: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:39:38.738 PM 11/22/2020
(Coding: 16# 1382 1B64 C772 494E 0810 7710)
Event 16 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:39:38.646 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 494E 0810 7710)
Event 17 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:39:34.265 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 18 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:39:16.220 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 19 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:38:53.755 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 20 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:38:52.694 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 21 of 117: Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
08:38:33.689 PM 11/22/2020
(Coding: 16# 494E FF8F C000 0000 0000 0000)
Event 22 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:38:11.190 PM 11/22/2020
(Coding: 16# 4302 FF68 C700 0000 0813 7713)
Event 23 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by stop switch being activated
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:38:11.189 PM 11/22/2020
(Coding: 16# 1381 1B64 C772 4303 0813 7713)
Event 24 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by stop switch being activated
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:38:11.097 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 4303 0813 7713)
Event 25 of 117: Event ID 16# 4303
STOP caused by stop switch being activated
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:38:08.148 PM 11/22/2020
(Coding: 16# 4303 FF84 0000 0000 0000 0000)
Event 26 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:37:15.972 PM 11/22/2020
(Coding: 16# 4302 FF68 C700 0000 0810 7710)
Event 27 of 117: Event ID 16# 1382
Request for automatic warm restart
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:37:15.971 PM 11/22/2020
(Coding: 16# 1382 1B64 C772 0000 0810 7710)
Event 28 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:37:15.879 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 0000 0810 7710)
Event 29 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:37:11.537 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 30 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:36:53.451 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 31 of 117: Event ID 16# 4358
All modules are ready for operation
Operating mode: STOP (internal)
Incoming event
08:35:08.774 PM 11/22/2020
(Coding: 16# 4358 FF44 0000 0000 0000 0000)
Event 32 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:35:03.023 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 33 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:35:01.966 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 34 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:34:32.941 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 35 of 117: Event ID 16# 4358
All modules are ready for operation
Operating mode: STOP (internal)
Incoming event
08:34:30.244 PM 11/22/2020
(Coding: 16# 4358 FF44 0000 0000 0000 0000)
Event 36 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:34:24.706 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 37 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:34:23.649 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 38 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:34:07.628 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 39 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:33:50.990 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 40 of 117: Event ID 16# 430E
Memory reset executed
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
Incoming event
08:33:47.756 PM 11/22/2020
(Coding: 16# 430E FF23 0000 0000 0000 0000)
Event 41 of 117: Event ID 16# 4308
Memory reset started by switch setting
Previous operating mode: STOP (internal)
Requested operating mode: STOP (memory reset)
Incoming event
08:33:45.225 PM 11/22/2020
(Coding: 16# 4308 FF42 0000 0000 0000 0000)
Event 42 of 117: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 5
No relevance for user (Z2): 0000 (Z3): 000f
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
08:32:20.484 PM 11/22/2020
(Coding: 16# 49A0 FF64 C17B 0005 0000 000F)
Event 43 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:32:20.479 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 8B07)
Event 44 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Input address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:32:20.479 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 0B07)
Event 45 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:32:20.418 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 0000 0814 1714)
Event 46 of 117: Event ID 16# 5962
Parameter assignment error preventing startup in party-line parameters/communication bus parameters
Error type: I/O not ready, i.e. a module has not entered a type ID within the module monitoring time
Operating mode: STOP (internal)
External error, Incoming event
08:32:19.767 PM 11/22/2020
(Coding: 16# 5962 FF04 C17B 0005 0000 000F)
Event 47 of 117: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 5
No relevance for user (Z2): 0000 (Z3): 000f
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
08:31:57.551 PM 11/22/2020
(Coding: 16# 49A0 FF64 C17B 0005 0000 000F)
Event 48 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:31:57.545 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 8B07)
Event 49 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Input address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:31:57.545 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 0B07)
Event 50 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:31:57.482 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 0000 0814 1714)
Event 51 of 117: Event ID 16# 5962
Parameter assignment error preventing startup in party-line parameters/communication bus parameters
Error type: I/O not ready, i.e. a module has not entered a type ID within the module monitoring time
Operating mode: STOP (internal)
External error, Incoming event
08:31:55.501 PM 11/22/2020
(Coding: 16# 5962 FF04 C17B 0005 0000 000F)
Event 52 of 117: Event ID 16# 5962
Parameter assignment error preventing startup in party-line parameters/communication bus parameters
Error type: I/O not ready, i.e. a module has not entered a type ID within the module monitoring time
Operating mode: STOP (internal)
External error, Incoming event
08:31:07.341 PM 11/22/2020
(Coding: 16# 5962 FF04 C17B 0005 0000 000F)
Event 53 of 117: Event ID 16# 5962
Parameter assignment error preventing startup in party-line parameters/communication bus parameters
Error type: I/O not ready, i.e. a module has not entered a type ID within the module monitoring time
Operating mode: STOP (internal)
External error, Incoming event
08:28:20.274 PM 11/22/2020
(Coding: 16# 5962 FF04 C17B 0005 0000 000F)
Event 54 of 117: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 5
No relevance for user (Z2): 0000 (Z3): 000f
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
08:24:37.908 PM 11/22/2020
(Coding: 16# 49A0 FF64 C17B 0005 0000 000F)
Event 55 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 0 of the module with parameter assignment errors
Error type: configurable slot empty
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:24:37.902 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0000 8B08)
Event 56 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Input address: 0 of the module with parameter assignment errors
Error type: configurable slot empty
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:24:37.902 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0000 0B08)
Event 57 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:24:37.902 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 8B07)
Event 58 of 117: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Input address: 256 of the module with parameter assignment errors
Error type: type ID not detected ID
Operating mode: STARTUP (warm restart)
External error, Incoming event
08:24:37.902 PM 11/22/2020
(Coding: 16# 5961 FF06 C17B 0001 0100 0B07)
Event 59 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:24:37.839 PM 11/22/2020
(Coding: 16# 4301 FF46 C772 0000 0813 7713)
Event 60 of 117: Event ID 16# 5962
Parameter assignment error preventing startup in party-line parameters/communication bus parameters
Error type: I/O not ready, i.e. a module has not entered a type ID within the module monitoring time
Operating mode: STOP (internal)
External error, Incoming event
08:15:53.112 PM 11/22/2020
(Coding: 16# 5962 FF04 C17B 0005 0000 000F)
Event 61 of 117: Event ID 16# 4959
One or more modules not ready for operation
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
External error, Incoming event
08:15:52.530 PM 11/22/2020
(Coding: 16# 4959 FF44 C000 0000 0000 0000)
Event 62 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:14:47.517 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 63 of 117: Event ID 16# 430E
Memory reset executed
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
Incoming event
08:14:44.283 PM 11/22/2020
(Coding: 16# 430E FF23 0000 0000 0000 0000)
Event 64 of 117: Event ID 16# 6326
Memory reset request due to memory replacement
Operating mode: STOP (memory reset)
Incoming event
08:14:42.376 PM 11/22/2020
(Coding: 16# 6326 FF02 C450 8001 0000 1B79)
Event 65 of 117: Event ID 16# 4546
STOP caused by CPU memory management
Previous operating mode: STOP (own initialization)
Requested operating mode: STOP (memory reset)
Internal error, Incoming event
08:14:40.609 PM 11/22/2020
(Coding: 16# 4546 FF32 C0C0 0102 0000 0000)
Event 66 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:14:40.609 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 67 of 117: Event ID 16# 6526
Memory reset request due to memory replacement
Operating mode: STOP (own initialization)
Internal error, Incoming event
08:14:40.608 PM 11/22/2020
(Coding: 16# 6526 FF03 0000 0000 0001 0102)
Event 68 of 117: Event ID 16# 6326
Memory reset request due to memory replacement
Operating mode: STOP (own initialization)
Incoming event
08:14:40.608 PM 11/22/2020
(Coding: 16# 6326 FF03 C450 8001 0000 1B79)
Event 69 of 117: Event ID 16# 4580
STOP: backup buffer contents inconsistent (no transition to RUN)
Previous operating mode: No voltage
Requested operating mode: STOP (internal)
Internal error, Incoming event
08:14:14.476 PM 11/22/2020
(Coding: 16# 4580 FFF4 0000 0002 0000 0000)
Event 70 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:14:14.473 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 71 of 117: Event ID 16# 430E
Memory reset executed
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
Incoming event
08:14:05.339 PM 11/22/2020
(Coding: 16# 430E FF23 0000 0000 0000 0000)
Event 72 of 117: Event ID 16# 6326
Memory reset request due to memory replacement
Operating mode: STOP (memory reset)
Incoming event
08:14:05.284 PM 11/22/2020
(Coding: 16# 6326 FF02 C450 8001 1B79 0000)
Event 73 of 117: Event ID 16# 4546
STOP caused by CPU memory management
Previous operating mode: STOP (own initialization)
Requested operating mode: STOP (memory reset)
Internal error, Incoming event
08:14:00.629 PM 11/22/2020
(Coding: 16# 4546 FF32 C0C0 8FFE 0000 0000)
Event 74 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:14:00.629 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 75 of 117: Event ID 16# 6522
Illegal module: replace module and reset memory
Operating mode: STOP (own initialization)
Internal error, Incoming event
08:14:00.629 PM 11/22/2020
(Coding: 16# 6522 FF03 0000 0001 0001 8FFE)
Event 76 of 117: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:13:39.686 PM 11/22/2020
(Coding: 16# 494E FF4F C000 0000 0000 0000)
Event 77 of 117: Event ID 16# 4358
All modules are ready for operation
Operating mode: STOP (internal)
Incoming event
08:13:13.513 PM 11/22/2020
(Coding: 16# 4358 FF44 0000 0000 0000 0000)
Event 78 of 117: Event ID 16# 4357
Module monitoring time started
Operating mode: STOP (internal)
Incoming event
08:13:09.040 PM 11/22/2020
(Coding: 16# 4357 FF44 0000 0000 0000 0000)
Event 79 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:13:07.984 PM 11/22/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 80 of 117: Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
08:37:18.943 AM 10/26/2020
(Coding: 16# 494E FF8F C000 0000 0000 0000)
Event 81 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:36:25.050 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 82 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:36:25.049 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 83 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:36:24.960 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 84 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:36:03.140 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 85 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:35:00.130 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 86 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:35:00.129 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 87 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:35:00.040 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 88 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:34:39.548 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 89 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:33:42.681 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 90 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:33:42.679 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 91 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:33:42.591 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 92 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:33:40.660 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 93 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:31:42.079 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 94 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:31:42.078 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 95 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:31:41.991 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 96 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:31:39.971 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 97 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:29:59.121 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 98 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:29:59.120 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 99 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:29:59.031 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 100 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:29:57.057 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 101 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:25:08.204 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 102 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:25:08.203 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 103 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:25:08.114 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 104 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:25:05.325 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 105 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:06:22.793 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0814 7714)
Event 106 of 117: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:06:22.792 AM 10/26/2020
(Coding: 16# 1381 1B64 C772 4304 0814 7714)
Event 107 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:06:22.704 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 4304 0814 7714)
Event 108 of 117: Event ID 16# 4304
STOP caused by PG stop operation or by SFB 20 "STOP"
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
08:05:56.580 AM 10/26/2020
(Coding: 16# 4304 FF84 0000 0000 0000 0000)
Event 109 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:04:41.840 AM 10/26/2020
(Coding: 16# 4302 FF68 C700 0000 0810 7710)
Event 110 of 117: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:04:41.839 AM 10/26/2020
(Coding: 16# 1382 1B64 C772 494E 0810 7710)
Event 111 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:04:41.750 AM 10/26/2020
(Coding: 16# 4301 FF46 C772 494E 0810 7710)
Event 112 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:04:37.298 AM 10/26/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 113 of 117: Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
04:22:52.342 PM 10/23/2020
(Coding: 16# 494E FF8F C000 0000 0000 0000)
Event 114 of 117: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
07:56:14.040 AM 10/23/2020
(Coding: 16# 4302 FF68 C700 0000 0810 7710)
Event 115 of 117: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
07:56:14.038 AM 10/23/2020
(Coding: 16# 1382 1B64 C772 494E 0810 7710)
Event 116 of 117: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
07:56:13.950 AM 10/23/2020
(Coding: 16# 4301 FF46 C772 494E 0810 7710)
Event 117 of 117: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
07:56:09.497 AM 10/23/2020
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
-
- Site Admin
- Posts: 1387
- Joined: Sat Aug 13, 2005 6:15 am
Re: [?]: CP 343-5 Fault when replace new CP
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number: 1002
DP master affected in rack 0 and slot 4
Station number: 0, slot number: 10
witch is dp-master on slot 4? what is station 0 with problem slot 10?RUS wrote:кто воткнут в 4 слот? что за станция 0 с проблемным слотом 10?
задняя шина между модулями установлена? ножки в модулях не погнуты?
убери всё , оставь только проц и коммукационик
backward bridge correctly installed?
remove all modules , configure cpu & cp only
-
- Posts: 8
- Joined: Tue Nov 12, 2019 9:12 am
Re: [?]: CP 343-5 Fault when replace new CP
All modules were removed and the project was rebuilt from scratch. Only Cpu and CP modules were added.
CPU slot 2.
CP is installed in Slot 4.
Hardware is configured accordingly.
I don't know why you wrote something like this!
https://wetransfer.com/downloads/83a981 ... 109/c1ec2f
Project and error files
CPU slot 2.
CP is installed in Slot 4.
Hardware is configured accordingly.
I don't know why you wrote something like this!
https://wetransfer.com/downloads/83a981 ... 109/c1ec2f
Project and error files
-
- Site Admin
- Posts: 1387
- Joined: Sat Aug 13, 2005 6:15 am
Re: [?]: CP 343-5 Fault when replace new CP
i am not understand are you not connect cp to cpu with black jumper? see "WhatsApp Video 2020-11-22 at 21.04.38 (1).mp4"
-
- Posts: 8
- Joined: Tue Nov 12, 2019 9:12 am
Re: [?]: CP 343-5 Fault when replace new CP
Yes, I connect it with the U connector.
(Video 2020-11-22 at 21.04.38) In this video U connected with connektor.
(Video 2020-11-22 at 21.04.38 (1)) In this video, it is not connected. It was to show that it works independently.
(Video 2020-11-22 at 21.04.38) In this video U connected with connektor.
(Video 2020-11-22 at 21.04.38 (1)) In this video, it is not connected. It was to show that it works independently.