Hi Everyone

I had to replace an HMI & the project Intouch 7.11 was converted to Intouch 2014 R2 SP1 version. The PLC is TSX Premium.

Installed the Intouch 2014 & DAServer & Configured. The problem is that there is no communication with the PLC. It was observed that the Device Group in the diagnostics is not found.
Else the Access Names is configured as for Access Name (checked in Windowmaker & Tag Dictionary). The pictures of the SMC & Access Name could be viewed on the web address below..

Any help in regard to the PLC communication with the Intouch would be much appreciated.

https://ibb.co/d2ZDMbh
https://ibb.co/xLzm4My
https://ibb.co/QkrbMVM
https://ibb.co/XJQkk7t
https://ibb.co/8j7DVpV

Thanks in advance.
Dr.Acrobat
Posts: 66
Joined: Sat Mar 10, 2007 8:11 am
Location: Spain

Re: Intouch 2014 communicatio to TSX Premium

Post by Dr.Acrobat »

Hello try remove Poste2 in node name if Intouch Viewer run on same machine is not necessary.
cmos
Posts: 34
Joined: Thu May 21, 2009 4:52 pm
Location: Europe

Re: Intouch 2014 communicatio to TSX Premium

Post by cmos »

Take a look here https://www.youtube.com/watch?v=46Nd8NMJylM

to see something in Diagnostics>Device Groups should an application request something from DAServer.
to make a test open excel and in a cell type
=applicationname|<devicegroup>!itemname
example
=DASMBTCP|Pump_Normal!level
where Pump_Normal is Device Groups name and level is Device Items name
Device Groups
Name Update Interval(ms)
Pump_Normal 1000
Device Items
Name Item Reference
level 1hr
hr means Holding Register equals in Premium PLC %MW1