[?]: CPU 319 BF3 flashing red

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
omar zedan
Posts: 244
Joined: Sat Oct 22, 2011 7:12 am

[?]: CPU 319 BF3 flashing red

Post by omar zedan »

Dear All
I have CPU 319 CPU connected to 3 Danfoss drive via profinet
(I connect my laptop to the hab and I found the PLC and the 3 Danfoss "the network is good"),
the BF3 flashing red and the diag. buffer
(IO access error writing P area, word access, Access address 2602 Request OB I/O access error OB (OB122), Priority class 1 External error, Incoming event)
the address 2602 dose not exist in hardware, also the OB122 used.
What can I do to solve this issue?
Thanks
georg_demmler
Posts: 75
Joined: Wed Nov 18, 2009 4:02 pm

Re: [?]: CPU 319 BF3 flashing red

Post by georg_demmler »

Hello,

what do you expected from the forum ?
That we guess what happens - please put some pictures about the online Hardwareconfiguration so we see the hardware.

What is the Event-ID of the diag. buffer? Is the equipment old or new.

How did you check "network is good".

We need a little bit more information if you want help from the forum.

In German we have a slang - here you have a bone look for the meat.

Thanks

Image
omar zedan
Posts: 244
Joined: Sat Oct 22, 2011 7:12 am

Re: [?]: CPU 319 BF3 flashing red

Post by omar zedan »

Dear georg_demmler
Nice to read from you, here is some meat :)
I use SIMATIC Manager v5.5 In HW Config when I go online I find all nodes (Profibus and Profinet nodes).
Also, I ping the 3 profinet nodes (after connecting my laptop to the hub) and I get a replay from all nodes.

The event ID is I/O access error, writing.

So sorry I get some problem (I do not able for uploading image in this form therefore I upload the dig. buffer image in link below)
https://mega.nz/file/XAgD2DIJ#t63oxdsji ... JCHmjNqDV0
Image

also project Link is:-
https://mega.nz/file/SFxhFbBI#eBl8_hbE4 ... McxGmXXRjY
(mirr) https://disk.yandex.ru/d/ZRa8W4J90Si--g
Thanks
CoMod
Site Admin
Posts: 3992
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia

Re: [?]: CPU 319 BF3 flashing red

Post by CoMod »

See Cross-reference table - PIW/PQW 2602 is used in FC91
Image
omar zedan
Posts: 244
Joined: Sat Oct 22, 2011 7:12 am

Re: [?]: CPU 319 BF3 flashing red

Post by omar zedan »

Yes, sir, I find this address (also there is PQW 2602), and when I try to use it in a variable table the status field in the variable table shows me nothing just a glass icon with a line inside it.
maybe something out of range? I don't know.
What is the glass icon inside the variable table (Status field)?
and how can I solve this issue?
Thanks
CoMod
Site Admin
Posts: 3992
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia

Re: [?]: CPU 319 BF3 flashing red

Post by CoMod »

this program downloaded from PLC

no symbol names :(
no comments :(
For decision need full source of Step7 project with symbol names and comments :) and documentation with schemes
эта программа скачана с ПЛК

нет названий, символьных имён :(
без комментариев :(
Для решения нужен полный исходник проекта Step7 с именами символов и комментариями :) и документация со схемами
Image Image
sania
Site Admin
Posts: 1387
Joined: Sat Aug 13, 2005 6:15 am

Re: [?]: CPU 319 BF3 flashing red

Post by sania »

это пустышка,
сотри букву Р , так и прогу не меняешь и лампочку погасишь
delete "P" in "PIW" / "PQW" it will not change program and correct the error
georg_demmler
Posts: 75
Joined: Wed Nov 18, 2009 4:02 pm

Re: [?]: CPU 319 BF3 flashing red

Post by georg_demmler »

Hello,

this is my only comment - it is nice to get a program without any symbolic.

So here is what I find - yes the program use the address 2602

Go to the hardware - select the part with the CPU 319 and on the slot X3 you find the CPU-CA140-1. Select this and you find the I-Device the address range
for inputs / outputs from 2600-2663.

But I don't know how its works.

Hope this helps
omar zedan
Posts: 244
Joined: Sat Oct 22, 2011 7:12 am

Re: [?]: CPU 319 BF3 flashing red

Post by omar zedan »

Thanks a lot, friends.
georg_demmler
Posts: 75
Joined: Wed Nov 18, 2009 4:02 pm

Re: [?]: CPU 319 BF3 flashing red

Post by georg_demmler »

Hello,

some information about your plc.

The program what you send is a I-device - that means you have a master and one (or more) I-devices.

The communication between the I-device and the master is over inputs and outputs.

You definied in the I-device the Inputrange and Outputrange - create a GSD-File and put this GSD-File in the Master-PLC.

You find a very helpful video in YT - Siemens SIMATIC Manager_Communication between two PLC Using I Device option (S7-300/S7-400)

And the read BF light shows, that the Master-PLC is missing.

KHS is a german company and let me guess - the program is working in a liquid area (filling and so on)

Hope this helps.
omar zedan
Posts: 244
Joined: Sat Oct 22, 2011 7:12 am

Re: [?]: CPU 319 BF3 flashing red

Post by omar zedan »

Thanks, Friend
You are right