I have CPU 319 CPU connected to 3 Danfoss drive via profinet
(I connect my laptop to the hab and I found the PLC and the 3 Danfoss "the network is good"),
the BF3 flashing red and the diag. buffer
(IO access error writing P area, word access, Access address 2602 Request OB I/O access error OB (OB122), Priority class 1 External error, Incoming event)
the address 2602 dose not exist in hardware, also the OB122 used.
What can I do to solve this issue?
Thanks
what do you expected from the forum ?
That we guess what happens - please put some pictures about the online Hardwareconfiguration so we see the hardware.
What is the Event-ID of the diag. buffer? Is the equipment old or new.
How did you check "network is good".
We need a little bit more information if you want help from the forum.
In German we have a slang - here you have a bone look for the meat.
Dear georg_demmler
Nice to read from you, here is some meat
I use SIMATIC Manager v5.5 In HW Config when I go online I find all nodes (Profibus and Profinet nodes).
Also, I ping the 3 profinet nodes (after connecting my laptop to the hub) and I get a replay from all nodes.
Yes, sir, I find this address (also there is PQW 2602), and when I try to use it in a variable table the status field in the variable table shows me nothing just a glass icon with a line inside it.
maybe something out of range? I don't know.
What is the glass icon inside the variable table (Status field)?
and how can I solve this issue?
Thanks
no symbol names
no comments
For decision need full source of Step7 project with symbol names and comments and documentation with schemes
эта программа скачана с ПЛК
нет названий, символьных имён
без комментариев
Для решения нужен полный исходник проекта Step7 с именами символов и комментариями и документация со схемами
this is my only comment - it is nice to get a program without any symbolic.
So here is what I find - yes the program use the address 2602
Go to the hardware - select the part with the CPU 319 and on the slot X3 you find the CPU-CA140-1. Select this and you find the I-Device the address range
for inputs / outputs from 2600-2663.