Mitsubishi MR-j4_GF can not set IP address

привода и частотники
KonstantK
Posts: 1
Joined: Sun May 12, 2024 9:29 pm

Mitsubishi MR-j4_GF can not set IP address

Post by KonstantK »

Hi to all

I have problem with servo amplifier Mitsubishi MR-j4-40GF-RJ
I can't to set IP address. In any cases there is 0.0.0.0. And impossible to change and so dosn't pinged from PC or can't finding by PLC FX5U.
SW1-1 - off, SW1-2 - on. So it choices CC Link Field Basic communication.
I try to set SW2 and SW3 in various positions for setting various ip address - but it doesn't affect
The led on LAN port CN1A lights green.

At same time the amplifier without problem connect with PC via usb.

When I try to set in MR Configurator2 in Parameter section the IP address I get a massage "The parameter is write-protected or the data that was written is incorrect"
In Also there is empty in Diagnostic - System Configuration - IP Address, though the MAC address is indicated

The permision is RW for all group fo parameters (PA19 (Parameter block) = 00AB

I don't understand what could be the reason