Connecting to a Micro 850 with disable ports

RSLinx, RSLogix, RSView, LogixPro ...
phophollety
Posts: 13
Joined: Thu Mar 05, 2015 6:49 pm

Connecting to a Micro 850 with disable ports

Post by phophollety »

Hello Mates,

Currently I've a second hand Micro850 (2080-L50E-48QBB) PLC, it turns on and goes straight to RUN, no faults, some outputs are on.

Cant connect with USB, port is disabled (have tested the PC and USB Cable with another unit, same model)
Cant connect through RS232 on DF1 (same, testes with another unit, I can talk with it on rslinx classic, so pinout is correct)
Cant find it on BootP or rslinx, I've no idea of its IP.
I do not have a the SDCARD module.

Some wireshark connection was kind inconclusive (as Im very very unused with wire shark)

So, how to connect and clear the PLC?

Greetings
sania
Site Admin
Posts: 1400
Joined: Sat Aug 13, 2005 6:15 am

Re: Connecting to a Micro 850 with disable ports

Post by sania »

why not connect over tcp?
you can try specify ip like 192.0.0.1 or 172.0.0.1 or 10.0.0.0
& subnet 255.0.0.0
try search and after this correct pc ip like in cpu & load empty program