S5 115 <-> PC communication problem

Post by kazzuro »

Hello,
I have a RS232-TTY converter which works properly with S5-95. But my PC cannot communicate throught this cable with S5-115U 943B. It is cable similar to this one:
Image
Do you know other solutions for communiaction between PC and S5?

My other problem is that my interface cannot communicate with any PLC when I use RS232-USB converter. Do you know why it doesnt work ?

Thanks!
Guest

Post by Guest »

To use an USB-converter with a SIEMENS RS232C - TTY interface or other is not functional because the signal which goes out the converter is not compatible with the signal which goes in the rs232c-tty interface.
burich
Posts: 10
Joined: Sun Jul 09, 2006 1:37 am
Location: Brazil

usb comunication with step5

Post by burich »

hi ,
the problem for comunication usb - rs232 is :
1) which is the version of step5 and windows you have?
all the version for step 5 run in dos mode with emulator for windows, and you can see the windows in the step5 but run in dos mode, ( i not test the last version step5 v7.23 for win XP ) but the other all run in dos mode with emulador for windows and the dos software can not abble the usb port and no go on-line with the plc s5 .
You understand , the problem is the software must be can run in windows mode , the only software manager the usb port is windows and not dos !
You must try with the last version on step5 v 7.23 and windows xp sp1,
i not try , but you can make the test!
best regards, pichi burich
kazzuro
Posts: 5
Joined: Fri Jun 09, 2006 6:35 am
Location: Poland

Post by kazzuro »

Thanx burich
I use WinXP with SP2 and IBHSoftec's: S5/S7 for Windows.