I saw the topic about how to connect WinCC with PLCSIM, but it does not fit for WinCC flexible.
I'm trying to test of S7 program on the PC with out 5611card. I have adjust the station configurator on the WCC flexible.
I can't insert a "SIMATIC S7 PROTOCOL SUITE" in the Tag Management and so on.
Only in communications/connections i can select communication driver.
Is it possible to connect WinCC flexible with PLCSIM installed at the same computer, and what actions i have to do?
Is this possible!?
Or mabey, somebody have some other better idea!?
Thanks for advance!
[?+]: How to connect WinCC flexible with PLCSIM
-
- Posts: 2
- Joined: Sun Jun 03, 2007 2:21 pm
- Location: Russia
-
- Site Admin
- Posts: 3992
- Joined: Thu Feb 16, 2006 3:25 pm
- Location: Russia
See http://support.automation.siemens.com/W ... n/13283804
If there is no MPI card installed in the configuration computer, then at least the PC adapter must be installed as interface for STEP 7.
Connect panel to MPI only.
If there is no MPI card installed in the configuration computer, then at least the PC adapter must be installed as interface for STEP 7.
Connect panel to MPI only.
in Russian wrote:Смотри аналогично ProTool. Связь с симулятором PLCSIM возможна только при назначении панели адреса MPI