hello guys,could you help me about link PC to s7-316DP via CP343-1?
the address for CP343-1 is 10.15.18.64
and I set my PC address 10.15.18.100
but when I select "display accessible node"
it shows no accessbile node
could you help me?
it would be nice of you to put up some picture for this problem
thanks a lot
[?]: how ot upload project to PC via cp343-1?
-
- Posts: 31
- Joined: Sat Sep 15, 2007 9:43 am
- Location: China
-
- Posts: 139
- Joined: Wed Sep 26, 2007 2:57 am
- Location: Philippines
-
- Posts: 3
- Joined: Wed Nov 14, 2007 12:42 pm
- Location: Europe
Hello,
It is CP343-1 or CP343-1 Lean ? We are using Lean's without any problem uploading and downloading projects from local or remote locations. One thing - you cannot connect PC with CP343 using "straight" cable, it must be crossed, or you have to use a normal ethernet switch with straight cables.
Check again your IP adresses in CP343 and PC including submasks.
out.
It is CP343-1 or CP343-1 Lean ? We are using Lean's without any problem uploading and downloading projects from local or remote locations. One thing - you cannot connect PC with CP343 using "straight" cable, it must be crossed, or you have to use a normal ethernet switch with straight cables.
Check again your IP adresses in CP343 and PC including submasks.
out.
-
- Posts: 31
- Joined: Sat Sep 15, 2007 9:43 am
- Location: China
when I choose "display accessible node"reymond_craig wrote:Hi,
I read something about this forgot where, Ill tell you once i recall it. It says that there are only supported (ex20-0aa0)that can be seen on the accessible nodes,. Are you able to ping the ip adress of the cp from your PG? If yes can you monitor the status of the PLC?
Warm regards,
Rey
I can see the stations
while I cannot ping the ip address of the CP
-
- Posts: 508
- Joined: Mon Jul 16, 2007 12:28 pm
- Location: Europe
Hibunglehead wrote:Is configuration of PLC loaded? (through MPI)..otherwise CPU will not be able to use CP
how it said bunglehead, you need MPI cable for download the address of the CP, I mean IP. But if this has been already done, check cable (type of cable - cross or straight, which you connect to the CP, and if you have some other device between PC and CP (swicth, hub), you can check also. And check also subnet mask of IP address (your - PC and CP must be the same)
regards
-
- Posts: 31
- Joined: Sat Sep 15, 2007 9:43 am
- Location: China
Umencho wrote:
how it said bunglehead, you need MPI cable for download the address of the CP, I mean IP. But if this has been already done, check cable (type of cable - cross or straight, which you connect to the CP, and if you have some other device between PC and CP (swicth, hub), you can check also. And check also subnet mask of IP address (your - PC and CP must be the same)
regards
what's the different between switch and hub?
I use straight cable.
-
- Posts: 508
- Joined: Mon Jul 16, 2007 12:28 pm
- Location: Europe
hi
about difference read here: http://www.duxcw.com/faq/network/hubsw.htm
For direct connection PC-CP you need crossover cable. If you are using switch you need 2 straight -thru cables
PC <-> Hub/Switch <-> S7-3**-PN/CP343/443
PC <-> S7-3**-PN/CP343/443
regards
about difference read here: http://www.duxcw.com/faq/network/hubsw.htm
For direct connection PC-CP you need crossover cable. If you are using switch you need 2 straight -thru cables
PC <-> Hub/Switch <-> S7-3**-PN/CP343/443
PC <-> S7-3**-PN/CP343/443
regards