[?]: PLC-PLC connection via radio modem using RS232/RS485

Post by ggmahyar »

In a project there are 7 PLCs communicating together with radio modems (output RS232) and the designer has considered CP341 (RS232) modules for the PLCs.

Q1: Does it work since we can not use any addressing? Can we use Modbus protocol with that module?

Q2: What shall we do to solve it? Change from RS232 to RS485 version?
rataman
Posts: 52
Joined: Sat Nov 25, 2006 2:53 am
Location: America

Post by rataman »

i used rs-485 with modbus library with s7-200, you can use rs232 also with radio links, it creates some kind of virtual cable, but use modbus. You should buy modbus donghles from siemens for that cpu and every thing will be fine.