(( Hi, I'm newbie to PLC world. So please don't laugh at my stupid question. )
I am trying to connect to a CJ1M CPU21 but the PLC seems does not detect my cable connection - RS232C. These conditions have been virified by me:
The CPU setup (CJ1M CPU21) is correct.
The connecting method is Toolbus.
The com port is correct ( in this case, I set the cable port to COM1)
The 5th dip switch in the PLC was on.
When I first pluged in my cable, the COMM indicator was light up, but if I tried to connect to PLC, it switched to off.
The cable I am using has been vefified and connected successfully to the other PLC (CQ1M...), but not the series CJ1M ???
In my case, do I fortget something important ??
[?]: How download program from CJ1M PLC ?
-
- Posts: 11
- Joined: Sun May 11, 2008 11:14 am
- Location: Vietnam
-
- Posts: 431
- Joined: Sat Oct 22, 2005 7:17 am
- Location: Europe
CJ1M, it never passed for my hands but I give a small help with manuals.
http://www.idom.ru/files/Omron/FA/Manuals/Plc's/
read 340, ..., 345, 380 and 336
the cable for CQM is not for CJ. i think
if to obtain what you intend says some thing because also I am interested for the future.
best regards
http://www.idom.ru/files/Omron/FA/Manuals/Plc's/
read 340, ..., 345, 380 and 336
the cable for CQM is not for CJ. i think
if to obtain what you intend says some thing because also I am interested for the future.
best regards
-
- Posts: 11
- Joined: Sun May 11, 2008 11:14 am
- Location: Vietnam
I've found the cable serial diagram of CQM1, anyone has the rest.
http://plcforum.uz.ua//O ... d.zip.html
The CJ1M and CQM1 actually share the same cable diagram. Look at this documentation.
http://plcforum.uz.ua//O ... g.pdf.html
Anyone has the experience with this ?? Please help !
http://plcforum.uz.ua//O ... d.zip.html
The CJ1M and CQM1 actually share the same cable diagram. Look at this documentation.
http://plcforum.uz.ua//O ... g.pdf.html
Anyone has the experience with this ?? Please help !
-
- Posts: 431
- Joined: Sat Oct 22, 2005 7:17 am
- Location: Europe
you did not look very well ...
this is the cable (if it is equal to CQM, ...I did not compare ...)
with switch 4 and 5 tries on off ....
with cx programmer chooses "Auto Online" or the "Sismac Way" in manual.
search with google this manual "W393_E1_07_CJ1_Operation_Manual.pdf" +- 12 Mb
this pdf have all that you need.
edit
http://plcforum.uz.ua//W ... l.rar.html
your cable is for HMI Proface (if it is equal ...i did not compare...)
regards
this is the cable (if it is equal to CQM, ...I did not compare ...)
with switch 4 and 5 tries on off ....
with cx programmer chooses "Auto Online" or the "Sismac Way" in manual.
search with google this manual "W393_E1_07_CJ1_Operation_Manual.pdf" +- 12 Mb
this pdf have all that you need.
edit
http://plcforum.uz.ua//W ... l.rar.html
your cable is for HMI Proface (if it is equal ...i did not compare...)
regards
-
- Posts: 21
- Joined: Mon Jun 30, 2008 2:32 am
- Location: Indonesia
Connect PLC CJ1M
You can try with this :
1. Turn On the dip switch pin 5
2. Set in your CX - programmer with default setting, baudrate 19200
3. check u Comm port, it must same with auto detect in your PC COMM
4. Using sysmac way Communication
5. Try to connect again.
Hope this help...
Husanto
1. Turn On the dip switch pin 5
2. Set in your CX - programmer with default setting, baudrate 19200
3. check u Comm port, it must same with auto detect in your PC COMM
4. Using sysmac way Communication
5. Try to connect again.
Hope this help...
Husanto