Can be used next configuration as PLC?
WinLC + CP5611 + ET200U + S5 digital I/O cards.
All the best and
Happy New Year !!!
dekor
[?]: WinLC + CP5611 + S5 digital I/O cards ?
-
- Posts: 114
- Joined: Wed Jan 03, 2007 9:10 pm
- Location: Europe
-
- Posts: 52
- Joined: Fri Jun 08, 2007 4:00 pm
- Location: Europe
From siemens forum :
be careful the ref of your ET200U in the lower reference you cant do Standard Dp, for the rest it's just programming ..With the ET200U (MLFB: 6ES5 318 8MB12 or 6ES5318-8MB13) you can use either the DP-SIEMENS- or the DP standard protocol. The protocol desired can be selected with the switch block of the interface module. If you are using an S7 master (e.g. CPU 316-2 DP), switch 8 must be switched on.